title: Best Data Center Power Monitoring Software in 2026
slug: best-data-center-power-monitoring-software
url: /topics/guides/best-data-center-power-monitoring-software/index.md
publishedAt: "2026-11-26T16:17:46"
updatedAt: "2026-11-26T16:17:46"
excerpt: "Last updated November 26, 2026. The short version: Schneider Electric EcoStruxure Power Monitoring Expert is the pick for power quality analysis across a large electrical system. Eaton Brightlayer EPMS fits operators that want electrical monitoring, data center infrastructure management (DCIM), and distributed IT monitoring on one platform. Siemens SENTRON Powermanager fits sites that run the [&hellip;]"
authors:
  - Reliable Media
  - Mike Ramsey
---

# Best Data Center Power Monitoring Software in 2026

By [Reliable Media](/authors/reliable-media/index.md), [Mike Ramsey](/authors/mike-ramsey/index.md)

Last updated November 26, 2026.

## Data Center Power Monitoring Software Comparison Table

"Start by listing what you need to see, from the utility feed to the rack," says Mike Ramsey, publisher of Reliable. "Coverage overlaps between these products, so ask each vendor to mark which of your devices its quote includes and which it leaves out."

## 7 Best Data Center Power Monitoring Software Platforms in 2026, Ranked by Use Case

The seven are ranked by use case. The first five center on the facility electrical system, and the last two on the rack, panel, and circuit level. Each "Not the best fit for" line is Reliable's editorial judgment, drawn from the vendor's published pages.

### 1. Schneider Electric EcoStruxure Power Monitoring Expert: Best for Power Quality Analysis Across a Large Electrical System

Schneider Electric EcoStruxure Power Monitoring Expert (PME) is electrical power monitoring software best suited to large data centers that need power quality analysis from the utility service down to the breakers. Schneider describes it as software for power-critical and energy-intensive facilities.

**What it covers.** PME groups related alarms into incidents and lays out the sequence of events on a timeline. It helps engineers investigate the cause and direction of voltage disturbances from waveforms recorded by supported meters. Schneider also lists monitoring of breaker protection settings, capacity tracking to avoid overloads, and location of insulation faults.

**Backup power and reliability reports.** PME produces a Generator Test report for emergency power supply systems, and the 2024 R3 release added calculated transfer time for ASCO automatic transfer switches. PME 2024 added SAIDI and SAIFI reliability reports and native connectivity to ASCO 7000 series transfer switches.

**Integration.** PME 2024 added an OPC UA server and client, COMTRADE import for analyzing events recorded by third-party devices, single sign-on through SAML, and TLS 1.3 encryption.

**Building management.** Schneider documents three links between PME and its EcoStruxure Building Operation BMS. Web services pass electrical data to the BMS, PME diagrams, dashboards, and reports embed in the BMS interface, and an ETL engine brings BMS history into PME. Schneider's February 18, 2026 roadmap post describes further connections across IT, electrical, and building systems.

**Control.** Schneider sells a separate product, EcoStruxure Power Operation, for electrical distribution monitoring and control. Its design guide describes high availability, redundancy, and high-speed data acquisition for very large sites with many devices. Buyers who need operator control should evaluate Power Operation alongside PME.

**Release and security.** The most recent release notes in Schneider's PME 2024 online help cover 2024 R3, dated October 2025. Those [release notes](https://product-help.schneider-electric.com/EcoStruxure/Power-Monitoring-Expert-2024/content/1_overview/whatsnew.htm) list fixes for path traversal, unsafe deserialization, and server-side request forgery issues. They also add Windows Server 2025 support.

**Deployment and pricing.** PME installs on Windows Server with a SQL Server database. Schneider's product page lists no price and routes buyers to a demo, to sales, or to a partner.

**Not the best fit for:** teams that want a hosted service at a published price. Schneider's release notes describe an installed Windows Server application.

### 2. Eaton Brightlayer EPMS: Best for EPMS, DCIM, and Distributed IT Monitoring on One Platform

Eaton Brightlayer EPMS is electrical power monitoring software best suited to operators that want the electrical system, the white space, and remote IT sites monitored on one platform. Eaton says its EPMS can be combined with Brightlayer DCIM and Brightlayer Distributed IT software, so every user works from the same normalized data.

**What it covers.** Eaton lists smart alarms for more than 30,000 equipment models, power quality and root-cause analysis tools, and waveform analysis with export to COMTRADE files. One-line diagrams show real-time status using ANSI and IEC symbols. The software also tracks water, air, gas, electricity, and steam use.

**Equipment.** Eaton's EPMS pages name medium-voltage and low-voltage switchgear, transformers, meters, relays, automatic transfer switches, PDUs, panelboards, uninterruptible power supply (UPS) systems, and bus duct. Eaton describes visibility into electrical assets "regardless of location or vendor."

**Two products.** Eaton sells Brightlayer EPMS and a second product, Foreseer EPMS. Eaton positions Foreseer for hyperscale data centers, with a customizable interface, user-defined formulas, and reports on power usage effectiveness (PUE), branch circuit loading, and energy consumption. Confirm which product a quote covers.

**What changed in 2026.** Eaton announced Brightlayer software release 8.1 in July 2026. With version 8, the sister products carry new names: Brightlayer DCIM, formerly Data Center Performance Management, and Brightlayer Distributed IT, formerly Distributed IT Performance Management.

**Support policy.** Eaton's [end-of-life policy](https://www.eaton.com/us/en-us/software/brightlayer/end-of-life-policy.html), updated July 29, 2026, lists EPMS 8.1 as current and 8.0 and 7.3 as supported. Eaton generally stops supporting major or minor versions more than two behind the current release, with an exception when releases come unusually often.

**Licensing and pricing.** Eaton says pricing is based on system size and selected extensions, every deployment gets all core EPMS features, and an annual maintenance contract is required. The software is typically installed on a dedicated server or virtual machine on the customer's network and is sold through authorized resellers. Eaton says DCIM and Distributed IT functions can be turned on within the same platform, so ask what each adds to the quote. Its EPMS pages list no price.

**Not the best fit for:** teams that upgrade software rarely, since Eaton's support generally covers the current version and the two before it. Buyers who need a published price will not find one on Eaton's EPMS pages.

### 3. Siemens SENTRON Powermanager: Best for Desigo CC Sites That Want the BMS and EPMS in One Interface

Siemens SENTRON Powermanager is power monitoring software best suited to data centers that run Siemens' Desigo CC building management system and want the electrical power monitoring system in the same interface. Siemens integrates Powermanager with Desigo CC, so EPMS and BMS data sit together.

**What it covers.** Powermanager monitors energy use and the condition of the power distribution system. Reports include cost center, load variance, Sankey, and top 10 consumer reports, and Siemens says they support energy management under ISO 50001. A health dashboard covers the whole system. For SENTRON 3VA and 3WA circuit breakers it shows health as a percentage along with expected remaining life.

**Power quality.** The PQ Advisor module assesses power quality against EN 50160, working with compatible Siemens SICAM Q100 and Q200 recorders over IEC 61850. It raises alarms for voltage deviations, harmonics, sags, swells, and transients.

**Why Siemens joins the two systems.** A Siemens flyer dated August 2025 says an EPMS time-stamps events to the millisecond and gives 5 to 60 seconds as a common BMS response time. Those are different specifications, so set time-stamp resolution, polling interval, and end-to-end alarm latency separately when the two systems are joined. Siemens cites Greenergy Data Centers in Estonia, which monitors power quality across high-voltage, medium-voltage, low-voltage, UPS, and third-party devices on an integrated platform.

**Scale and pricing.** Siemens says Powermanager supports SENTRON devices and third-party devices, with a published upper limit of 1,000 devices per server. The U.S. product page lists no price or license terms.

**Not the best fit for:** operators with no plan to run Desigo CC, since the single-interface case rests on it. Sites approaching the published limit of 1,000 devices per server should ask Siemens for a sizing calculation and a validated multi-server design.

### 4. Vertiv Unify: Best for Colocation and Hyperscale Builds That Want Factory-Commissioned Monitoring

Vertiv Unify is integrated monitoring and control software best suited to colocation and hyperscale builds that want power and thermal systems delivered under one interface. Vertiv [launched Unify on March 18, 2025](https://www.vertiv.com/en-us/about/news-and-events/corporate-news/new-vertiv-software-strengthens-visibility-and-control-of-the-complete-power-train-and-thermal-chain-for-colocation-and-hyperscale-data-centers/) as a unified control platform for critical power and thermal infrastructure.

**What it covers.** Vertiv describes monitoring and control across power (EPMS), thermal (BMS), and building management systems. The architecture scales out for high-availability and fully redundant designs.

**Licensing.** Vertiv describes an unlimited licensing model. It says buyers can add unlimited clients, screens, tags, connections, and designers. Those terms describe software licensing, so price hardware and services separately.

**Deployment.** Vertiv says its equipment arrives pre-tested and pre-commissioned at the factory, and it lists on-site, hybrid, and cloud deployment. Site integration and acceptance testing still apply. Third-party systems connect through open industrial protocols, which the product page leaves unnamed.

**Services and pricing.** Vertiv sells remote monitoring services for UPS systems, thermal equipment, and rack PDUs, built on its LIFE Services technology and separate from the Unify license. The Unify product page lists no price and points buyers to Vertiv sales or a reseller.

**Not the best fit for:** enterprise server rooms and small sites, which sit outside the colocation, hosting, and hyperscale audience Vertiv's page addresses. Retrofit sites with equipment from several makers should get the supported protocol and device list in writing.

### 5. ABB Ability Data Center Automation: Best for Industrial-Grade Control of Power and Cooling

ABB Ability Data Center Automation is monitoring and control software best suited to operators that want mechanical, electrical, and IT infrastructure data on one industrial automation platform. ABB describes it as control, monitoring, and optimization for mission-critical infrastructure, with BMS, EPMS, and DCIM capabilities in a single solution.

**What it covers.** The platform integrates data from IT, power, cooling, and building systems. It shows one view across sites at the enterprise, floor plan, zone, system, and component levels. ABB says it automates cooling and electrical systems, and its web portal updates PUE every minute.

**Background and partners.** IT asset management and DCIM come through an integration with FNT, a partner extension to confirm in the quote. ABB's page lists case studies from Ericsson, NEXTDC in Australia, and Lakeland Community College in the United States.

**Related ABB software.** ABB also sells Ability Energy and Asset Manager for Data Centers, which adds a real-time PUE widget, an asset health view, and maintenance planning based on predictive analytics.

**Deployment and pricing.** ABB lists on-premise and hybrid cloud deployment. Its page lists no price and directs buyers to a contact form or a channel partner.

**Not the best fit for:** teams that want packaged rack PDU monitoring they can install themselves. ABB calls the product an "integration and automation platform," which points to an engineered project.

### 6. Sunbird Power IQ: Best for Multi-Vendor Rack PDU Monitoring at a Published Price

Sunbird Power IQ is data center power monitoring software best suited to teams that monitor rack PDUs from several manufacturers and want a published price. Sunbird [lists Power IQ at $66 per node per year](https://www.sunbirddcim.com/pricing) as a U.S. offer, with a one-year commitment paid up front.

**What it covers.** Sunbird calls Power IQ its "PDU polling engine." It monitors rack PDUs, floor PDUs, UPS systems, remote power panels, busways, branch circuit meters, and environment sensors. The feature list includes three-phase balance, circuit breaker state changes, rack PDU configuration and firmware updates, energy billback, and support for AC and DC power.

**Third-party devices.** Sunbird lists free plugins for third-party PDUs, UPS systems, and remote power panels. Users, sites, and data points are unlimited.

**Licensing.** Power IQ is licensed by node, which covers a monitored item such as a rack PDU. Sunbird's cabinet packages include two node licenses for two networked rack PDUs per cabinet, and more nodes can be bought for UPS systems, remote power panels, cooling units, floor PDUs, and rack transfer switches. Buyers choose an annual subscription or a perpetual license with annual maintenance.

**Deployment.** Sunbird lists deployment on VMware, Microsoft Hyper-V, Nutanix, Linux KVM, and Amazon Web Services, and it quotes a hosted version separately. Sunbird offers a 30-day free trial with the buyer's own data.

**What changed in 2026.** Power IQ 9.3.5, released July 6, added a workflow for bulk PDU configuration. Power IQ 9.3.7 followed on October 26 and calculates active power from current and voltage for DC facility items.

**Not the best fit for:** electrical engineers who need waveform forensics and protection-settings monitoring on switchgear. Sunbird positions Power IQ as DCIM monitoring software built around PDU polling. Buyers outside the United States should confirm pricing, since the published offer is valid in the U.S. only.

### 7. Packet Power EMX: Best for Wireless Retrofits of Circuit, Panel, and Busway Metering

Packet Power EMX is power and environmental monitoring software best suited to operating data centers that need circuit, panel, or busway metering added without Ethernet cabling to every monitoring point. Packet Power sells wireless monitors that send readings to an Ethernet gateway, which can forward data to its EMX Energy Portal or serve it to third-party monitoring software.

**What it covers.** The hardware range includes smart AC power cables, embedded AC monitors, panel monitors, and 48-volt DC monitors. One high-density monitor covers up to 120 circuits. Environmental monitors cover temperature, humidity, leaks, and differential pressure.

**Software.** EMX shows readings and history for each monitor and includes built-in reports. Panel maps set up in the monitoring system tie measurements to individual circuits for display in EMX. Packet Power's documentation describes EMX as a cloud portal that can be installed locally in some cases.

**Integration.** The monitors report by radio to an Ethernet gateway on the site's IP network. The gateway serves data over SNMP and Modbus TCP/IP, so a site can poll it from an existing BMS or DCIM system with or without EMX. The company reports more than 250,000 monitoring devices deployed in 40 countries.

**Installation.** The wireless link cuts network cabling to each monitoring point, and electrical connections and commissioning are still required. Depending on the DC monitor, installation can involve integrated or remote current sensors, shunt adapters, and power leads that also give the voltage reference.

**Pricing.** Packet Power's site lists no prices, including for an EMX subscription. EMX is optional for sites that collect readings through the gateway in another monitoring system.

**Not the best fit for:** sites that already have networked meters and intelligent rack PDUs and need software only. Packet Power's site covers metering and environmental monitoring and names no waveform analysis for power quality.

## Top EPMS Software Vendors for Data Center Electrical Distribution Monitoring and Control

Five of the seven ranked products are sold as an EPMS or include one. They are Schneider Electric EcoStruxure Power Monitoring Expert, Eaton Brightlayer EPMS and Foreseer EPMS, Siemens SENTRON Powermanager, Vertiv Unify, and ABB Ability Data Center Automation.

Monitoring and control are separate jobs. An EPMS measures, records, and alarms. Control means an operator can act on equipment from the screen.

Schneider sells EcoStruxure Power Operation for electrical distribution monitoring and control. Vertiv describes Unify as monitoring and control across power and thermal systems. ABB describes control and automation of cooling and electrical systems. Siemens points buyers who want power automation to its Sm@rtGear platform.

Ask each vendor which actions an operator can take from the software, who is permitted to take them, and which are locked out by design.

## Power Monitoring and Analytics Software for AI Data Center Campuses

**Scale.** Published scale figures describe different products, so treat them as separate facts. Siemens publishes a limit of 1,000 devices per Powermanager server. Schneider's February 2026 roadmap post says a single server of Data Center Expert, its rack-level monitoring product, will support up to 4,000 devices under SNMPv3. Sunbird's Power IQ 9.1.0 release notes added collection and roll-up of power readings above one megawatt.

**Liquid cooling.** Schneider says EcoStruxure IT Expert and Data Center Expert gained liquid cooling monitoring in 2025 through its Motivair integration. Sunbird's separate dcTrack product added tracking and modeling of liquid cooling infrastructure in release 9.3.5 on July 6, 2026.

**Dense and DC-powered racks.** Sunbird lists support for AC and DC power, and Packet Power sells 48-volt DC monitors along with its 120-circuit monitor. Neither statement tells you whether a product supports higher-voltage DC distribution. Ask each vendor to confirm the voltage class, metering point, sampling rate, waveform capture, polling interval, and alarm latency for your design.

"Rack loads are climbing faster than most monitoring plans were written for," says Reliable publisher Mike Ramsey. "Ask each vendor how the software handles a row that doubles its load, and how quickly a new circuit or busway shows up on screen."

## EPMS, BMS, and DCIM: What Each One Monitors

**EPMS.** An electrical power monitoring system gives near real-time and historical visibility into the electrical system, from switchgear and generators to UPS systems and panels. Eaton notes that an EPMS is often the best way to meet the monitoring requirements of MasterSpec section 26 09 13, a design specification section for electrical monitoring.

**BMS.** A building management system runs mechanical systems such as chillers, pumps, and air handlers. Event time stamps, sampling rates, polling intervals, and alarm delivery times are separate specifications. Compare them one by one when a BMS and an EPMS will share data.

**DCIM.** Data center infrastructure management software tracks assets, capacity, and change in the white space, and it often monitors rack PDUs. Sunbird Power IQ and several products under Also Considered sit in this group. The groups overlap: Eaton's EPMS lists PDUs, and Power IQ monitors UPS systems and busways.

**PUE.** Power usage effectiveness divides total facility energy by IT equipment energy over the same period. Both totals can come from one metering system or from several. A live power ratio on a dashboard and PUE calculated from energy over a reporting period are separate measures.

**PUE reporting in the European Union.** [Commission Delegated Regulation (EU) 2024/1364](https://eur-lex.europa.eu/eli/reg_del/2024/1364/oj) requires operators of data centers in the European Union with an installed IT power demand of at least 500 kW to report energy data each year. Reports go through a national scheme where a member state has one, and otherwise directly to a European database. The first reports were due September 15, 2024, and the date is now May 15 each year.

## What Changed in Data Center Power Monitoring in 2026

**Eaton renamed its entry-level tool.** On July 1, Eaton rebranded Intelligent Power Manager as Brightlayer Distributed IT - Lite, which still supports up to 50 licenses.

**Schneider kept tying its monitoring products together.** Its February roadmap post describes a new web interface for Data Center Expert and further connections among EcoStruxure IT, PME, and EcoStruxure Building Operation.

## How to Choose Data Center Power Monitoring Software

### 1. Should you standardize a data hall on one power distribution vendor: Eaton, Vertiv, or Schneider?

Standardizing can reduce integration work, because native device integrations cut engineering effort, although coverage varies by vendor and device. Vertiv ships Unify pre-commissioned with Vertiv equipment. Schneider's PME has native connectivity to its ASCO transfer switches. Eaton builds its EPMS on the same platform as its DCIM and Distributed IT software.

Native connectivity is no guarantee of a lower project cost, and a supported protocol is no guarantee that a device reports every reading. All three vendors say they monitor other makers' devices. Ask for a demonstration that uses one of your second-source devices, and check which readings, time stamps, and alarms come through.

### 2. Which PDU monitoring tool fits power usage and capacity planning?

Sunbird Power IQ reports available capacity by cabinet and simulates a rack power failover. Hyperview maps power path dependencies and tracks kWh. Server Technology's Sentry Power Manager trends power use and estimates when a threshold will be crossed, for Server Technology PDUs.

Start with the rack PDU brands you own. A single-brand site can use that maker's tool. A site with several brands needs software that polls all of them.

### 3. Who patches and upgrades the software?

An installed EPMS leaves patching with the owner's team. Schneider's PME 2024 R3 notes list security fixes that reach a site only when someone installs the release. Eaton's policy generally ends support for versions more than two behind the current release.

Hosted products move application updates to the vendor, on the terms of the contract. Sunbird quotes a hosted version of Power IQ, and Hyperview runs as a cloud service. Gateways, device firmware, integrations, and meter calibration stay with the operator or its integrator.

"A monitoring system that nobody maintains goes blind one device at a time," says Mike Ramsey, publisher of Reliable. "Put meter checks, firmware updates, and alarm reviews on the maintenance schedule the day the system goes live."

### 4. What does a small data center need, and what does it cost?

A small site can start at the rack. At Sunbird's published price, software subscriptions for 40 rack PDUs cost $2,640 a year. For U.S. customers, Hyperview [lists $3 per asset per year](https://www.hyperviewhq.com/pricing) with a 500-asset minimum, a floor of $1,500 a year before add-ons. A Sunbird node and a Hyperview asset are different billing units, and both figures exclude taxes, hardware, and services.

Feature sets vary among rack-level tools, and the ones in this guide are sold for rack and room monitoring, with event forensics left to an EPMS. Waveform analysis also depends on meters and relays that can capture waveforms. A site with its own switchgear and generators should price an EPMS as well.

## Also Considered

Six more products fit narrower cases.

* **Schneider Electric EcoStruxure IT Expert and Data Center Expert.** Schneider's rack-level and room-level monitoring software for UPS systems, rack PDUs, and cooling. IT Expert is a cloud service sold by node count, and Data Center Expert runs on premises.
* **Eaton Brightlayer Distributed IT.** Eaton's software for UPS systems and PDUs across edge and branch sites. The Lite edition, formerly Intelligent Power Manager, supports up to 50 licenses.
* **Hyperview.** Cloud DCIM with power monitoring, a power path dependency map, and kWh reporting in its base plan at $3 per asset per year. The optional control feature costs $1 per subscribed asset per year at U.S. pricing and needs supported hardware.
* **Modius OpenData.** DCIM software that Modius says bridges operational technology and IT, covering power, cooling, and environmental data in the white space and the gray space. It runs on premises or in the cloud, with a free trial.
* **Legrand Server Technology Sentry Power Manager.** Central management, trending, and scheduled reports for Server Technology rack PDUs, with a documented API for BMS and DCIM systems.
* **EkkoSense EkkoSoft Critical.** Cooling optimization software that lists a power monitoring module. It fits sites where the power question is tied to thermal performance.

## How We Evaluated

Independent editorial analysis based on public vendor documentation, vendor pricing pages, dated press releases, and vendor support and security pages. Pages were reviewed in November 2026.

Reliable does not sell data center power monitoring software, implementation services, or consulting and has no commercial interest in routing readers toward any particular vendor. Reliable does not accept payment for rankings. Vendors may sponsor enhanced listings with additional detail, but editorial rankings are independent. [Read our editorial policy](https://reliamag.com/editorial-policy/).

Each product was assessed on six criteria: the layer of the power chain it monitors, power quality analysis, third-party device support as the vendor states it, deployment options, pricing transparency, and release and support policy. No analyst reports or review-site ratings were used. A price cell marked quoted means the vendor's product pages show no public list price and route buyers to sales.

## Honest Limitations

* Vendor pages describe what a product is sold to do. How it performs in a particular facility depends on the meters installed, the network, and the integrator.
* Prices are those published in late November 2026. Sunbird's price is a U.S. offer. The other six ranked vendors show no public list price on their product pages, and resellers or marketplaces may still show one.
* Product names and editions in this category change, so confirm every function against the current data sheet.
* Third-party device support is as each vendor states it, and a protocol match does not prove a device will report every reading. Ask for the supported device list and test your own equipment before you sign.
* Metering design belongs with a qualified electrical engineer. That includes where meters go, how current transformers are sized, and how protection is coordinated.
* The field is wider than seven products. Building management vendors and independent integrators also deliver power monitoring, and this guide does not rank them.

## Frequently Asked Questions

### What is the best data center power management software?

The best choice depends on the layer you need to monitor. For the facility electrical system, Reliable's picks are Schneider Electric EcoStruxure Power Monitoring Expert for power quality analysis and Eaton Brightlayer EPMS for platform breadth. For rack PDUs from several makers, the pick is Sunbird Power IQ, at $66 per node per year. Packet Power EMX fits sites that need metering added without Ethernet runs to every meter.

### Can Schneider Electric's electrical power monitoring system and BMS run one data center better than Siemens?

Both vendors offer an integrated EPMS and BMS. Schneider integrates Power Monitoring Expert with EcoStruxure Building Operation, and Siemens integrates SENTRON Powermanager with Desigo CC. Reliable did not find an independent head-to-head test of the two. Compare them on the equipment you already own, the control functions you need, device support, commissioning, and service coverage.

### Who are the top providers of remote monitoring as a service for data center power and cooling systems?

The large equipment makers sell it. Vertiv offers remote monitoring of UPS systems, thermal equipment, and rack PDUs, staffed by its own specialists. Schneider's EcoStruxure IT Expert is cloud software for remote visibility, with dispatch services offered on top of it for some equipment, and Eaton lists remote monitoring within its Brightlayer portfolio. Ask who watches the alarms, during which hours, and what the response commitment is.

### What is the difference between an EPMS and DCIM?

An EPMS centers on the electrical system: switchgear, generators, transformers, UPS systems, and distribution panels, with power quality analysis and one-line diagrams. DCIM software manages assets, space, and capacity in the white space and often monitors rack PDUs. The two overlap, and Eaton and ABB offer both on one platform, ABB with partner integrations where required. Many sites run an EPMS for the electrical rooms and DCIM for the racks.

### Does data center power monitoring software calculate PUE?

Several products do. ABB says its Data Center Automation portal updates PUE every minute. Eaton lists PUE reporting in Foreseer EPMS, and Sunbird lists real-time PUE in Power IQ. PUE is total facility energy divided by IT equipment energy over the same period, so the figure depends on where the meters sit.

### How much does data center power monitoring software cost?

Sunbird Power IQ costs $66 per node per year in the United States, and Hyperview lists $3 per asset per year for U.S. customers, with a 500-asset minimum. The EPMS platforms from Schneider Electric, Eaton, Siemens, Vertiv, and ABB show no public list price on their product pages. An EPMS quote should itemize software licenses, meters and gateways, integration labor, commissioning, and annual support.

## Related Guides

* [Best DCIM Software for Data Center Operators](https://reliamag.com/topics/guides/best-dcim-software)
* [Best Energy Management Software for Industrial Facilities](https://reliamag.com/topics/guides/best-energy-management-software-industrial-facilities)
* [NFPA 70B Compliance: What Changed and When It Actually Applies](https://reliamag.com/topics/guides/nfpa-70b-compliance)
* [Electrical Equipment Failure Rate Benchmarks and Their Limits](https://reliamag.com/topics/maintenance-and-reliability/electrical-equipment-failure-rate-benchmarks)
* [MTBF and MTTR Benchmarks by Equipment Type: What Holds Up](https://reliamag.com/topics/guides/mtbf-and-mttr-benchmarks-by-equipment-type)

## Sources

* Schneider Electric: [EcoStruxure Power Monitoring Expert](https://www.se.com/us/en/product-range/65404) (product page, PME 2024 release notes, EcoStruxure Power design guides, and February 18, 2026 EcoStruxure IT post)
* Eaton: [Electrical power monitoring systems](https://www.eaton.com/us/en-us/software/brightlayer/datacenters-brightlayer/eaton-epms.html) (EPMS pages and FAQ, Brightlayer end-of-life policy, and July 2026 product announcements)
* Siemens: [SENTRON Powermanager](https://www.siemens.com/en-us/products/sentron/powermanager/) (product page, data center BMS and EPMS integration page, and August 2025 flyer)
* Vertiv: [Vertiv Unify Integrated Platform Software](https://www.vertiv.com/en-us/products-catalog/monitoring-control-and-management/software/vertiv-unify/) (product page, March 18, 2025 release, brochure, and remote services page)
* ABB: [ABB Ability Data Center Automation](https://new.abb.com/industrial-software/datacenter-automation) (product pages and Energy and Asset Manager for Data Centers page)
* Sunbird: [Now Available: Power IQ 9.3.7](https://www.sunbirddcim.com/blog/now-available-power-iq-937) (release posts, pricing page, and Power IQ data sheet and release notes)
* Packet Power: [Packet Power](https://www.packetpower.com/) (product pages and support documentation)

*Last updated November 26, 2026. This guide is editorial analysis by Reliable.*